I need to troubleshoot a jittery monitor and want to try an alternative isolation transformer.

I only have a spare 110v (input) isolation transformer so would need to power it from a step down/step up transformer outputting 110v.

Question is - if the step down/step up transformer is already isolating the power from the mains, so do I need a separate isolation transformer?
 

andyman

always pull away from your face
Credits
1,059CR
No...simple answer...all transformers (almost) are isolating transformers
smiley1.gif
 

justez

Newbie
Credits
38CR
The step down / up are usually autotransformers, they are not
usually isolated, but you have isolation transformers with different
outputs for different voltages.

This is 230V in and 230 or 115V out

Captura11.png


You can also use an isolation one in front of the voltage network, and then a step down / up to the chassis
 

Retroman839

Senior Member
vacBacker
Feedback
13 (100%)
Credits
8,292CR
step down transformers aren’t isolating. ( one lot windings )

Isolating transformers are isolating ( two lots of windings separated by magnets )

All transformers transform

Check it is isolating...

Most monitors are either 100v - 115. or 220 -250

A variac is a luxury you can gradually increase voltage ( less chance blowing components.

I might have a spare isolation
But can’t look till next week..
 

ataridude74

Active member
Feedback
4 (100%)
Credits
265CR
I guessed it wasn't isolating when the neutral showed continuity from primary to secondary, live didn't show continuity. I tested it on the monitor anyway (staying well clear of the chassis) and didn't make any difference, picture still jittery.

Good to know for future reference though, thanks all.
 