Do transformers go weak eventually?

RGP

Meeter & Greeter
Feedback
5 (100%)
Credits
2,039CR
So here's a weird situation...

In a cab, there is an isolation transformer.

When it was installed, its unloaded output from a 240v input was about 135v

When a monitor was loaded onto it, the voltage dropped to about 128v

This has been fine for at least 3 years......

Now, the monitor decided to go into shutdown. We removed the monitor from the machine thinking the PSU section had gone squiffy and proceeded to test.

It was a bit of an imperfect situation so we used a long lead from the cab to the chassis and measured the B+ - it was 186vDC so yes, it was going into shutdown.

We went over the PSU section and replaced the parts we thought were wrong and re-attached it to the power supply but it did the same.

While drinking a brew and scratching our heads we decided to measure the input voltage - it was 165v

Hmmmmmmmmmmm........

so we tried a different ISO block which we measured at 135v and hey presto, the monitor works again perfectly and was bench tested for a good 2+ hours before being declared ready to return to the machine.

If transformers are based on inductance based on ratio of turns - no direct or electronic limiting - whatever voltage in will get you a ratio out - 245v input to a 2:1 ratio will get you about 123v out.

So my question is - what can cause the voltage to change in the transformer?
 

Mitchell Gant

Active member
vacBacker
Feedback
2 (100%)
Credits
888CR
Enamel insulation on the wire in the primary or secondary windings can break down, particularly under high temperatures, and that shorts out windings that will change the ratio. As well as running even hotter causing more breakdown, etc.
 

RGP

Meeter & Greeter
Feedback
5 (100%)
Credits
2,039CR
Mitchell Gant said:
Enamel insulation on the wire in the primary or secondary windings can break down, particularly under high temperatures, and that shorts out windings that will change the ratio. As well as running even hotter causing more breakdown, etc.

Right, I understand, so ultimately they have a shelf life but its variable based on operating temperature causing some effects over a long term.

Time for a replacement transformer then.

Also, I suppose that if you had multiple input points - say 220v and 240v then if you set it to the lower and you have higher input voltage you'd get an odd output as well?
 

Mitchell Gant

Active member
vacBacker
Feedback
2 (100%)
Credits
888CR
RGP said:
Right, I understand, so ultimately they have a shelf life but its variable based on operating temperature causing some effects over a long term.

It's not really fair to say they have a shelf life, the transformer in the substation next door to my workshop has a date if 1968 stamped on it!

If it's overladed or maybe a poor quality transformer then that can cause the problem, but generally transformers are VERY reliable.

RGP said:
Also, I suppose that if you had multiple input points - say 220v and 240v then if you set it to the lower and you have higher input voltage you'd get an odd output as well?

If you wired 240V mains to the 220V transformer tapping then you will indeed get a higher output voltage. You'll also overheat it risking the shorted turns problem. If you put a much higher voltage in then you risk core saturation and at that point the transfomer appears like a short piece of wire with mains power across it. BANG!
 